That would be a 120 volt service, if it were the service equipment, and would be acceptable there.

However, being as it is a *PANEL* *AND NOT SERVICE EQUIPMENT* (arrrrgggg to the 'sub' thing - it is a "panel") ... (sorry had to get that out of my system) ... then bonding the neutral to ground *is not allowed*.