Re: p-trap
Quote:
Originally Posted by Jeff Eastman View Post
No ADA anywhere I could visibly see.

Thanks, I 'll write it up as an improperly sized trap system.
I would not say "improperly sized trap" as that trap looks to be "properly sized".

I would simply state improperly trapped, which includes the tailpiece (lack thereof) and improper bends. Unless that is an actual approved trap system, those 90 degree bends should have a larger radius to them - those look like pressure fittings, not DWV fittings - not the trap is glued up into the 90 degree elbow above, creating a lip to catch debris on and clog the trap (unless this is actually an approved trap system, in which case the inside of the 90 elbow above would be reduce to match up with the inside of the piece below.
__________________
Jerry Peck, Construction / Litigation Consultant