View Single Post
  #12 (permalink)  
Old 04-14-2007, 11:06 AM
Jerry Peck Jerry Peck is online now
Member
 
Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 7,765
Re: Multiple neutrals under same lug
Quote:
Originally Posted by Todd Erickson View Post
and then said but if the panel states it is rated for this, it is OK. We read the fine print on the panel and sure enough it did state that two wires could terminate under one lug. Now the question is, is this still wrong even though the manufacture states it is OK?
Nope not allowed, regardless, not for those size conductors.

What you read, I am assuming - because it is in most panels, is that two GROUNDING or *equipment ground* conductors are allowed.

NOT two "neutrals" or "groundED conductors".

Only when you get to paralleled conductors, which must be 1/0 and larger, is that allowed, and only then *if the terminal is identified* for more than one conductor.
__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )