2 service panels, 1 ground
Home has one 300 amp supply, a 200 amp primary and a 100 amp secondary panel. Secondary panel was NOT a sub (auxillary) panel as it had it's own feed from one of the lugs off of the meter.

SEC was fed through panel # 1 (directly behind meter) to go into panel #2 (about 1 foot away from panel #1) using rigid metal conduit to bond the 2 panels together.

Panel #1 had #6 ground to grounding rod.
Panel #2 had no ground conductor attached to the bus bar from a ground source.

Questions:

1. Is this considered to be using panel #1 as conduit? (I say it does)

2. Is the bonding of the panels sufficient to ground panel #2? (I say no)

If not:
3. Can panel #2 be grounded to the same grounding rod as panel #1 or should it have a separate grounding rod?
4. Are you allowed to bond main panels?
5. If a separate grounding rod is used, does the 8' clearance between rods apply when the panels are side by side?


I did refer this service to an electrician for repairs of loose grounds, oversized breakers and an improperly wired GFI breaker and suggested that the electrician evaluate the grounding of these panels. Any information learned will be useful in the future.
Attached Images
File Type: jpg Panel Setup.jpg (49.3 KB, 76 views)
__________________
Integrity Inspection Service, LLC
www.irsindy.com
(317) 345-1828

Last edited by Jon Randolph : 10-11-2007 at 05:44 PM. Reason: to add my Picasso rendition of panels
Reply With Quote
Are inspection referrals from past clients important to you?
If so, click here to get even more referrals!