View Single Post
  #12 (permalink)  
Old 11-29-2007, 07:54 PM
Jerry Peck's Avatar
Jerry Peck Jerry Peck is online now
Member
 
Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 14,297
Re: External Air Source
Quote:
Originally Posted by Jim Luttrall View Post
IRC 2003 R1005.1
Factory built or masonry fireplaces covered in this chapter shall be equipped with an exterior air supply to assure proper fuel combustion unless the room is mechanically ventilated and controlled so that the indor pressure is neutral or positive.

I don't see the wording you mention in my 2003 IRC, is there a change in the 2006 Jerry?
Yes, that is the difference and that is why we need to specify year of the code reference - this is from the 2006 IRC.
- R1005.1 Listing.
Factory-built chimneys shall be listed and labeled and shall be installed and terminated in accordance with the manufacturer’s installation instructions.

The 2006 has a completely different R1005.1 than the 2003 IRC has.

I say "potatoes" and you say "tomatoes", and everyone looks at as like we must be crazy.

R1005.1 in 2003 is talking about "tomatoes" and R1005.1 in 2006 is talking about "potatoes".

__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )
www.AskCodeMan.com
Reply With Quote