Re: Elbows in T & P drain pipe
Quote:
Originally Posted by charles buell View Post
Richard, there is also #5 in the 2006.

5. Discharge to the floor, to an indirect waste receptor
or to the outdoors. Where discharging to the outdoors
in areas subject to freezing, discharge piping
shall be first piped to an indirect waste receptor
through an air gap located in a conditioned area.
Charles,

#5 is referring to where the discharge from the air gap can discharge to.

FIRST do #2, THEN you have to drain that 'somewhere' and #5 tells you where you are allowed to drain that to.