Re: needed a breeze in the shower
Not sure where Michael's picture is from, possibly an older version of the NEC but here is what is said in the:

02 NEC:

410.1 Scope.
This article covers luminaires (lighting fixtures), lampholders, pendants, incandescent filament lamps, arc lamps, electric-discharge lamps, the wiring and equipment forming part of such lamps, luminaires (fixtures), and lighting installations.

410.4 Luminaires (Fixtures) in Specific Locations.

(A) Wet and Damp Locations. Luminaires (fixtures) installed in wet or damp locations shall be installed so that water cannot enter or accumulate in wiring compartments, lampholders, or other electrical parts. All luminaires (fixtures) installed in wet locations shall be marked, “Suitable for Wet Locations.” All luminaires (fixtures) installed in damp locations shall be marked, “Suitable for Wet Locations” or “Suitable for Damp Locations.”

(D) Bathtub and Shower Areas. No parts of cord-connected luminaires (fixtures), hanging luminaires (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub or shower stall.

The intent of 410.4(D) is to keep cord-connected, hanging, or pendant luminaires and suspended fans out of the reach of an individual standing on a bathtub rim. This list of prohibited items recognizes that the same risk of electric shock is present for each one.

Exhibit 410.1 illustrates the restricted zone in which the specified luminaires, lighting track, and paddle fans are prohibited. This requirement applies to hydromassage bathtubs, as defined in 680.2, as well as other bathtub types and shower areas. See 680.43 for installation requirements for spas and hot tubs (as defined in 680.2) installed indoors.