Originally Posted by
Jerry Peck
Hope you don't mind me quoting you separately - but it is the only to logically answer this.
.... you are trying to apply different requirements and intermingle them with each other. Apply each separately.
No problem, I'm not touchy about such things.
- 1. Closer than 10 feet (3048 mm) to an appliance vent outlet, a vent opening from a plumbing drainage system or the discharge outlet of an exhaust fan, unless the outlet is 3 feet (914 mm) above the outside air inlet.
In the case of a natural draft gas appliance vented to the exterior, what is the "
appliance vent outlet" at the interior with violates the 10' requirement in (1) above, the draft hood?