View Single Post
  #4 (permalink)  
Old 01-11-2008, 10:37 AM
Joe Tedesco's Avatar
Joe Tedesco Joe Tedesco is offline
Member
 
Join Date: Mar 2007
Location: USA
Posts: 21
Re: Opening in service panel enclosure
I would call attention to:

300.7 Raceways Exposed to Different Temperatures

(A) Sealing Where portions of a cable raceway or sleeve are known to be subjected to different temperatures and where condensation is known to be a problem, as in cold storage areas of buildings or where passing from the interior to the exterior of a building, the raceway or sleeve shall be filled with an approved material to prevent the circulation of warm air to a colder section of the raceway or sleeve.

Is the cabint enclosing the panelboard on the other side? If so, can you post a picture with the cabinet front removed, close up image showing all if the interior, please.

PS: I would also cite the damaged insulation on Phase B.
__________________
Joe Tedesco

Last edited by Joe Tedesco : 01-11-2008 at 10:41 AM. Reason: More
Reply With Quote