Re: Double wired breaker
Quote:
Originally Posted by Jerry Peck View Post
BUT ... (that big 'but') ...

You DID notice that ONLY applies to the *15 amp* breaker, right?

Not listed or allowed for the 20 amp breaker.
As the original creator and poster of that highlighted photo (from May, 2005) I have to say you are wrong there. The wire size ranges apply to everything within that section...in this case 10 to 30 amps. Otherwise, the 25 and 30 amp breakers are allowed no wires. That wouldn't make much sense.