Re: Is PB the only Black line?
Quote:
Originally Posted by Reis Pearson View Post
This is a water service line, not waste. Is ABS used for service? I've never seen that?
2006 IRC, Table P2904.4, Water Service Pipe, does list ABS as suitable for use as "water service pipe", however, Table P2904.5, Water Distribution Pipe, does NOT list ABS as being allowed for "water distribution pipe".

Also: (bold and underlining are mine)
- P2904.4 Water service pipe. Water service pipe shall conform to NSF 61 and shall conform to one of the standards listed in Table P2904.4. Water service pipe or tubing, installed underground and outside of the structure, shall have a minimum working pressure rating of 160 pounds per square inch at 73°F (1103 kPa at 23°C). Where the water pressure exceeds 160 pounds per square inch (1103 kPa), piping material shall have a rated working pressure equal to or greater than the highest available pressure. Water service piping materials not third-party certified for water distribution shall terminate at or before the full open valve located at the entrance to the structure. Ductile iron water service piping shall be cement mortar lined in accordance with AWWA C104.

I.e., if the water service pipe is not also approved for water distribution pipe, it must terminate 'outside the structure' - and, if that is ABS in the photo, it does not.
__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )

Last edited by Jerry Peck : 01-26-2008 at 12:15 PM.
Reply With Quote