Just to name a few thing I see in there:
- As stated by others - no dead front cover.
- What does that safety switch operate? Has the switching guts been removed?
- The neutral on the 240 volt circuit is connected to ground.
- The ground terminal is most likely only rated for one conductor and has at least 3 conductors in it (3 are visible).
- As stated by others - no low voltage is allowed in there with the power circuit conductors.
- There is a good potential for the bare ground to come in contact with a hot terminal.