View Single Post
  #13 (permalink)  
Old 02-07-2008, 04:46 AM
Richard Moore's Avatar
Richard Moore Richard Moore is offline
Member
 
Join Date: Mar 2007
Location: Seattle, WA
Posts: 247
Re: Washer Machine outlet, GFCI protected?
Quote:
Originally Posted by Tim Moreira View Post
Hi gang,

Laundry sink about two feet away from washing machine outlet. It is not GFCI protected. I would think it should be due to the proximity of the sink.

Agreed?
As Jerry stated, the 2008 NEC now covers this without exceptions...- - - (7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink.

However (and I'll ask Jerry to check me on this) prior to 2008 (2005?) the 6ft rule was only for wet bar sinks (and then earlier than that, for kitchen sinks). I don't believe there was a rule prior to 2008 that actually covered laundries or laundry sinks. The upshot, as far as I can determine, is that in an existing home the washer receptacle (or any other receptacle) within 6ft of a laundry sink was not required by the NEC to be a GFCI, unless the room also happens to be a bathroom.

So...definitely a good idea to recommend a GFCI as an inexpensive saftey upgrade but it's probably not a "mandatory" repair you could defend with code.
__________________
Richard Moore
Rest Assured Inspection Services - www.rainspect.com
Seattle, Washington
Reply With Quote