Thanks Michael,
Yep, my bad.
I only had the 2002 and 2008 versions on hand when I posted.
Those changes were indeed made in the 2005 NEC and not 2008.
GFCI Requirements Expand in 2005 NEC
......
Section 210.8(A)(7), which formerly covered GFCI protection for 15- and 20-ampere receptacles serving wet bar countertops and located within six feet of the wet bar countertop, has been revised. This subsection has been expanded to cover 15- and 20-ampere, 125-volt receptacles within six feet of the outside edge of dwelling-unit laundry sinks, utility sinks and wet bar sinks at any height. Since this section now covers laundry sinks and utility sinks, as well as wet bar sinks, the reference to countertops has been deleted. This means any 15- and 20-ampere, 125-volt, single-phase receptacle within six feet of these sinks must be GFCI protected. This would apply to receptacles located from the floor level up to six feet above the sink, including receptacles mounted in the ceiling but still located within the six-foot dimension from the edge of a counter-mounted laundry, utility or wet bar sink.
So..."required" after 2005, recommended "upgrade" for older homes.