Originally Posted by Gunnar Alquist View Post
Are they required when the house is supplied by a private well? I would think so, and reported as such, but since the query, I have been unable to find any specific code.

Gunnar,


P2902.1 General.
A potable water supply system shall be designed and installed as to prevent contamination from nonpotable liquids, solids or gases being introduced into the potable water supply. Connections shall not be made to a potable water supply in a manner that could contaminate the water supply or provide a cross-connection between the supply and a source of contamination unless an approved backflow-prevention device is provided. Cross-connections between an individual water supply and a potable public water supply shall be prohibited.

P2902.3 Backflow protection.


A means of protection against backflow shall be provided in accordance with Sections P2902.3.1 through P2902.3.6. Backflow prevention applications shall conform to Table P2902.3, except as specifically stated in Sections P2902.4 through P2902.5.5.
(followed by a listing of 6 types of backflow devices)

P2902.4 Protection of potable water outlets.


Potable water openings and outlets shall be protected by an air gap, reduced pressure principle backflow preventer with atmospheric vent, atmospheric-type vacuum breaker, pressure-type vacuum breaker or hose connection backflow preventer.
(followed by a listing of 3 examples)

I should add: I am presuming by your question that both the house and the landscape sprinkler system are provided by the same well.