View Single Post
  #4 (permalink)  
Old 04-26-2007, 10:37 PM
Richard Rushing's Avatar
Richard Rushing Richard Rushing is offline
Member
 
Join Date: Mar 2007
Location: Duncanville, Tx
Posts: 1,086
Re: Rafters larger than ridge
Hello Gregg,

For future reference, here is the IRC back up for the requirement;

R802.3 Framing details. Rafters shall be framed to ridge board or to each other with a gusset plate as a tie. Ridge board shall be at least 1-inch (25.4 mm) nominal thickness and not less in depth than the cut end of the rafter. At all valleys and hips there shall be a valley or hip rafter not less than 2-inch (51mm) nominal thickness and not less in depth than the cut end of the rafter. Hip and valley rafters shall be supported at the ridge by a brace to a bearing partition or be designed to carry and distribute the specific load at that point. Where the roof pitch is less than three units vertical in 12 units horizontal (25-percent slope), structural members that support rafters and ceiling joists, such as ridge beams, hips and valleys, shall be designed as beams. installed to bearing walls at a slope not less than 45 degrees from the horizontal. The braces shall be spaced not more than 4 feet (1219 mm) on center and the unbraced length of braces shall not exceed 8 feet (2438 mm).

Hope this helps...

Rich
Reply With Quote