Originally Posted by
Mike Boyett
Nolan, if the proposed new Texas SOP ever makes it thru committee and is accepted then the requirement to operate the T&P valve goes away for us.
Not according to the latest draft of the SOP... (bold is mine)
(m) Water heaters. The inspector shall inspect the unit(s) and:
(1) report the energy source;
(2) report as Deficient:
(A) inoperative unit(s);
(B) leaking or corroded fittings or tank(s);
(C) broken or missing parts or controls;
(D) the lack of a cold water shut-off valve;
(E) if applicable, the lack of a pan and drain system and the improper termination of the pan drain line;
(F) an unsafe location;
(G) burners, burner ignition devices or heating elements, switches, or thermostats that are not a minimum of 18 inches above the lowest garage floor elevation, unless the unit is listed for garage floor installation;
(H) the lack of protection from physical damage to the unit;
(I) a temperature and pressure relief valve that:
(i) does not operate manually;
(ii) leaks;
(iii) is damaged;
(iv) cannot be tested due to obstructions;
(v) is corroded; or
(vi) is improperly located;
There is a departure provision:
(n) Specific limitations for water heater. The inspector is not required to:
(1) verify the effectiveness of the temperature and pressure relief valve discharge piping or pan drain pipes;
(2) operate the temperature and pressure relief valve if the operation of the valve may in the judgment of the inspector cause damage to persons or property; or