Thread: Loose neutral.
View Single Post
  #8 (permalink)  
Old 04-14-2008, 12:16 PM
Jerry Peck Jerry Peck is offline
Member
 
Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 8,257
Re: Loose neutral.
Quote:
Originally Posted by Steve Brooks View Post
Jerry, What I was pointing out is the panel itself should be bonded to the grounding electrode conductor (To the water pipe, or ground rod). This effectively prevents the panel from ever being electrified. That was the question.
As for it being an abandoned wire inside the panel, that's a different finding, seperate from the current question.
Steve,

Because this is, according to David, a "downstream panel", it would be connected with an equipment grounding conductor, not to the grounding electrode conductor, water pipe or ground rod. Yes, the 'equipment grounding conductor' does need to go back to the service equipment, and thus back to the grounding electrode conductor, etc., it will not be connected to them, as is my take on what you said.

There just is not enough of the panel in that photo to show how this is "grounded".
__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )
Reply With Quote