Re: Service and load side panels in close proximity
Quote:
Originally Posted by Michael Thomas View Post
When the load side panel is in such close proximity to the service panel, and bonded in this manner, is it still considered a load side panel, or is it now part of the "service equipment" ?
It is still "separate".

The dangers of the problem are now reduced to that conduit, but the load side panel is still "non-service equipment" and the neutral needs to be isolated from ground.