Re: Power to both buss bars
WOW !! WOW !!!

The box under the meter is a terminal box only and contains no fuses ( It says it right in the photo ) ....

The service needs to be replaced , any State or local electrical inspector would have the power company take it off the grid unit it was replaced.....

There should be a disconnect with a 60 amp breaker installed in front of the panel to protect the service entrance , which isn't worth protecting ...... Then you have to seperate the grounds ( HA HA what grounds ) and neutrals because the panel thats there becomes a sub panel.......

It should all be replaced , none of it is worth saving....

The only thing protecting the service is the Fuse out on the Primary side of the transformer ......

Dave in NH