Re: Ventilation Required?
Quote:
Originally Posted by Ted Menelly View Post
No matter what the reasoning for leaving ventilation off it is not correct.
To the contrary, and that was what Brandon was pointing out - that there is an approved design which allows for sealed attics.

To write those up as lacking ventilation would be in error.

Quote:
As far as calling for every 150 square feet requiring 1 squre foot of ventilation I don't read that just because it is under 150 square feet it doesn't need any.
Exactly what I was pointing out. That ventilation/attic space is a ratio, not a bottom limit of attic space.

All based upon the code stating (underlining is mine) "The total net free ventilating area shall not be less than 1/150 of the area of the space ventilated".
__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )