Re: WH gas Flue Vent
Brian, every B-vent mfr sells a "draft hood adapter or connector" which is your transition piece from single walled pipe to B-vent.
Do you have a report on this black foam as having passed ASTM E-136, which is a 1382F vertical tube furnace? This test utterly destroys type X sheetrock and even Wonderboard. Not sure where you're getting your info. but I can assure you foam insulation indeed is considered combustible.
You just made the point why you don't screw through B-vent into single walled pipe. That's why you use single walled pipe only below B-vent into a draft hood connector, which is made to be screwed into the bottom part while the top uses a std. Bvent twist or snap lock depending upon mfr. You also just explained why almost every HVAC tech installs B-vent improperly---The supply houses don't sell them the proper connector.
Once you are running B-vent, you cannot revert back to single walled pipe in mid run, esp. at a firestop. Also, single walled adjustable elbows are notorious for blowing apart and must be properly supported. Explain to be how you transition from B-vent to single wall back to B-vent while still maintaining the listing all in one run.
There are two single walled pipes in these pics: the adjustable ell at the firestop and the one at the draft hood.
Bob
__________________
disgusted with some people on this forum. Out of here!
Last edited by Bob Harper : 05-17-2007 at 07:36 PM.
|