1- eq. grnds & neutrals to same bus bar on down stream panel(s)
AND that top ground terminal bar is not isolated from the enclosure, NO neutrals should be on it, period.

Then there is the ground on the other neutral terminal bars lower down on the left and the right. Looks like a ground bond screw needs to be removed from the neutral bar metal piece which connects the 2 lower neutral terminal bars together (when the neutrals are relocated down to these neutral terminal bars).

Plus the other issues raised by the others.

Yep, what a wasted effort.

Was this done with a permit? Contact Noel at the building department there in Destin. Show her the photo, she will likely want to know where it is.