Re: PVC conduit and outlet installed at service panel
As Wayne said, it all ain't right.

That PVC is pressure water pipe and not electrical listed, as well as being too sharp of a bend, just plain old not allowed for electrical use.

That's not the correct type of flashing for the mast and they screwed it up even more with that cable.

Crimeny, they sure boogered up that enclosure by installing that receptacle like that.

That is also service equipment and there are not supposed to be more than 6 mains, I count around 15, depending on if one is tied together with handle ties.

That is plain old "all wrong" and needs to be replaced with proper service equipment.