Thread: Basement egress
View Single Post
  #9 (permalink)  
Old 06-14-2007, 09:37 PM
Jerry Peck Jerry Peck is online now
Member
 
Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 7,773
Re: Basement egress
Quote:
Originally Posted by Bob White View Post
gotta be at least 20" wide, right? (the opening, that is....)

It's also only 4 sq ft instead of 5 sq ft opening size.

What was the measured width of the stair treads between the rails? 36" minimum, I hope.

What about the riser height and the tread depth?

Just way to many things to go wrong there, and the two you've provided measurements on are both wrong ... so there is no way to make the rest 'right', even if the stair is 'wide enough' and the risers and treads 'are correct', that does not offset the fact that the width and size are both too small.

Add to that, if that room is 12' x 12', the opening size needs to be 5.76 sf just to met minimum natural ventilation.

And twice that for minimum natural light, twice 5.76 = 11.52, and twice the opening size of 4 = 8,

So not we have (if that room is 12' x 12') four things wrong - MINIMUM - with that window.
__________________
Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com )
Reply With Quote