View Full Version : TPR discharge pipe



Richard Roshak
10-11-2008, 01:44 PM
Tell me this is wrong. I'm refering to code check (IRC 2803.6.1 and UPC 608.5). AS you can see this was an approved installation.
Rich

wayne soper
10-11-2008, 01:56 PM
" THIS IS WRONG" cannot be facing up. Must be able to see termination also. Could you?

Jerry Peck
10-11-2008, 05:07 PM
That NM cable is wrong too.

Looks like that is in a closet, in which case it would also require a disconnect to disconnect the water heater from its supply. (There is an exception for the disconnect, but with what is shown in that photo, I doubt it applies.)

Is that discharging into PVC in the corner behind the water heater? If so, that is not allowed either.

Joshua Hardesty
10-13-2008, 05:50 PM
Wow. That's a whole lot of effort to do something completely wrong.

The icing on the cake, though, are the two APPROVAL stickers on the side of that thing.