View Full Version : 3 taps Cutler Hammer



Ron Bibler
12-02-2008, 12:51 AM
Why would they have 3 taps on the breaker?

Cutler-Hammer Type CHAF - One Pole Arc Fault. 15 amp.

Best

Ron

Jerry Peck
12-02-2008, 07:04 AM
Not sure what you are referring to as taps, but AFCI breakers, like GFCI breakers, have a terminal to which the hot conductors goes, a terminal to which the neutral conductor goes, and a white pigtail which goes to the neutral terminal bar.

Ron Bibler
12-02-2008, 08:19 AM
Jerry they have 3 white wires in the lower back of this breaker?

and 1 Black in the breaker?

Best

Ron

Jim Luttrall
12-02-2008, 08:55 AM
See if this diagram make sense.
From this site Arc Fault Circuit Interrupteurs AFCI (http://www.arcadvisor.com/afci.html#WiringDiagram)

Jerry Peck
12-02-2008, 10:06 AM
Ron,

From the photo, there are two AFCI breakers side-by-side, I think the "3rd" white wire is actually to the other AFCI breaker. If not, that AFCI breaker is missing its 2nd white wire.

Ron Bibler
12-02-2008, 10:20 AM
Thanks Jerry. its was hard to see back behind everything and did not want to stick my hand back in there. I have other minor issue with this panel. will let sparky look at it.

Best

Ron