View Full Version : AC Primary drain vent



imported_John Smith
05-17-2007, 04:57 PM
I have seen several of these lately with tape over the open end. Sorry I dont have a picture, but try to envision the small vertical vent pipe (~ 6" in length) next to the evaporator coil. I skimmed the IRC, but didnt see anything about it.

Jerry Peck
05-17-2007, 05:57 PM
Vent should be on opposite side of trap from AHU.

If not, it only serves as a clean out, and allows air to be sucked in or blown out, wasting energy (and, if sucking in, sucks in unfiltered air).

imported_John Smith
05-18-2007, 06:09 AM
Yes, the vent is downstream of the trap. Im starting to question my understanding of this. I thought the vent was supposed to be open and not taped over or capped. I havent missed some new rule or change in physics have I?

Jerry Peck
05-18-2007, 06:13 PM
Yes, the vent is downstream of the trap. Im starting to question my understanding of this. I thought the vent was supposed to be open and not taped over or capped. I havent missed some new rule or change in physics have I?

If it is downstream of the trap, it could be a vent, and would be open.

If it is upstream of the trap, it could be a cleanout access, and would be capped.