Quick question regarding electrical.

Here's the setup:


Exterior automatic gate opener for a driveway
Wired back to panel which goes to ground
The motor is bolted to a steel frame on which the support pole is in the ground about 24"
Is this sufficiently bonded?
Is a GFCI breaker required?

Any help would be appreciated. Thanks

Roland Miller
02-04-2009, 06:25 PM
Not a real clear picture. An equipment grounding conductor is required to be pulled with the branch circuit.

It may need to be GFCI protected depending on the burial depth based on 300.5.

Ron Bibler
02-04-2009, 06:28 PM
How do you known its in the ground 24'?

How far away from the panel is the gate?

Can you see the panel from the gate?

Best

Ron

JB Thompson
02-04-2009, 06:28 PM
Not a real clear picture. An equipment grounding conductor is required to be pulled with the branch circuit.

It may need to be GFCI protected depending on the burial depth based on 300.5.

I don't have the clear picture either. It is being described to me by someone else.

The grounding conductor was pulled and connected properly within the panel enclosure.

Thanks for the 300.5 ref. I'll check it out.

Jim Luttrall
02-04-2009, 06:30 PM
If it is on a duplex outlet, it needs GFCI. Hard wired, maybe not.
I know of no bonding requirement for the gate or fence unless near a pool, but not a bad idea.

JB Thompson
02-04-2009, 06:32 PM
How do you known its in the ground 24'?

Owner observed it being installed


How far away from the panel is the gate?

60 ft


Can you see the panel from the gate?

Best

Ron

I don't know

JB Thompson
02-04-2009, 06:33 PM
If it is on a duplex outlet, it needs GFCI. Hard wired, maybe not.
I know of no bonding requirement for the gate or fence unless near a pool, but not a bad idea.

Hard wired

Jerry Peck
02-04-2009, 06:51 PM
It may need to be GFCI protected depending on the burial depth based on 300.5.

Roland,

Post the 300.5 code reference stating said requirement.

Roland Miller
02-04-2009, 07:33 PM
Hopefully the attachment is here

JB Thompson
02-04-2009, 08:04 PM
I'm having trouble seeing it. Are those requirements for GFCI?

Roland Miller
02-04-2009, 08:38 PM
I apologize--I just upgraded to office 07 and the scan function is not working so I had to cut and paste. Jerry --would you post the table 300.5 since you have the software??

Jerry Peck
02-04-2009, 08:59 PM
It does not lay the table out properly to copy and paste.

Here is a screen capture of the table.

It took me a while to figure out what you were referring to, but you are referring to the reduction in burial depth allowed with GFCI protection on residential branch circuits.

Column 4 is what Roland is referring to.

Roland Miller
02-04-2009, 09:02 PM
Thanks--I think I got my scanner running..:)

JB Thompson
02-04-2009, 09:06 PM
If I'm reading that right...it is saying that the assumption is that GFCI is required and the wire should be buried at 12" (the only applicable one for my situation).

So...currently, this is not GFCI protected. I'm still confused if that is required. We'd have to install a GFCI breaker.

What about the bonding? Any ideas there?

Thanks for the posts.

Roland Miller
02-04-2009, 09:06 PM
Lets see if this is clear.. You need Adobe Reader and you should be all set..

Roland Miller
02-04-2009, 09:09 PM
Are you asking about bonding the metal gate itself? Only the motor frame is required to be bonded.

JB Thompson
02-04-2009, 09:10 PM
Are you asking about bonding the metal gate itself? Only the motor frame is required to be bonded.

I'm asking if the motor being bolted to the steel frame is adequate.

Jerry Peck
02-04-2009, 09:14 PM
I'm asking if the motor being bolted to the steel frame is adequate.

No. The motor must be grounded with the equipment grounding conductor in with the circuit conductors.

Roland Miller
02-04-2009, 09:14 PM
The motor bolted to the steel frame is enough. There is actually no code requirement to bond the gate. There may be a manufacturers requirement to bond the gate. You may have to contact them..

Jerry Peck
02-04-2009, 09:23 PM
If I'm reading that right...it is saying that the assumption is that GFCI is required and the wire should be buried at 12" (the only applicable one for my situation).

So...currently, this is not GFCI protected. I'm still confused if that is required. We'd have to install a GFCI breaker.

No, that table is saying that, without GFCI protection, you need to follow the depths shown in Columns 1, 2, or 3 as applicable to the wiring method used. It is also saying that if you have GFCI protection installed, you can take advantage of a reduction in depth as shown in Column 4.

That means that if direct burial cable was used, the burial depth is (All locations not specified below) 24", however, let's say they buried the cable 18" deep (such as it was planned to use PVC with a depth of 18") - BIG OOPS! - but, if GFCI protection is installed, that cable now only requires being buried 12", thus it is now okay.

Yes, Column 4 can be used "to plan" a lesser depth, but it is most frequently used to 'correct for' an unplanned lesser depth for direct buried cable.

After all, why use it to get to 12" if you used a method in Column 2 which only required 6" depth? There is no reduction in depth there.

Jerry Peck
02-04-2009, 09:25 PM
Are you asking about bonding the metal gate itself? Only the motor frame is required to be bonded.


"Grounded", not "bonded"

JB Thompson
02-04-2009, 09:47 PM
No. The motor must be grounded with the equipment grounding conductor in with the circuit conductors.

Sorry I'm dense. Grounding aside... the motor does not have to be bonded such as pool pump motors do?

The motor is wired with a grounding conductor that travels to the panel and thus to the driven copper rod.

Jerry Peck
02-04-2009, 09:55 PM
Sorry I'm dense. Grounding aside... the motor does not have to be bonded such as pool pump motors do?

That's what I thought you were talking about - no.

Roland Miller
02-04-2009, 09:55 PM
Well Jerry here we go--The NEC doesn't use the term grounded in regard to the motor. It uses bonded and connected, avoiding the use of the term grounded. 250.102, 250.8, 250.110 250.112, 250.119 and 250.148. About as close as they get is calling it bonded and connected.. So the motor is (according to the NEC) "bonded" to the equipment grounding conductor. So Bonded is a more correct term according to the NEC..

Jerry Peck
02-04-2009, 10:05 PM
Well Jerry here we go--The NEC doesn't use the term grounded in regard to the motor. It uses bonded and connected, avoiding the use of the term grounded. 250.102, 250.8, 250.110 250.112, 250.119 and 250.148. About as close as they get is calling it bonded and connected.. So the motor is (according to the NEC) "bonded" to the equipment grounding conductor. So Bonded is a more correct term according to the NEC..

From the 2008 NEC. (underlining and bold are mine)
- VI. Equipment Grounding and Equipment Grounding Conductors
- - 250.112 Fastened in Place or Connected by Permanent Wiring Methods (Fixed) — Specific.
- - - (C) Motor Frames. Motor frames, as provided by 430.242.
- - - (D) Enclosures for Motor Controllers. Enclosures for motor controllers unless attached to ungrounded portable equipment.

- 430.242 Stationary Motors.
- - The frames of stationary motors shall be grounded under any of the following conditions:
- - - (1) Where supplied by metal-enclosed wiring
- - - (2) Where in a wet location and not isolated or guarded
- - - (3) If in a hazardous (classified) location
- - - (4) If the motor operates with any terminal at over 150 volts to ground
- - Where the frame of the motor is not grounded, it shall be permanently and effectively insulated from the ground.

Roland,

There sure are a lot of "grounded", "grounding", and "ground" terms in there regarding those motors.

A.D. Miller
02-05-2009, 05:03 AM
Also check the manufacturer's installation instructions for the requirement of a ground rod. Some require this:

Roland Miller
02-05-2009, 11:24 AM
Yup--Jerry --it will be confusing until you learn to read English.. Grounded is the (past tense) end result of bonding (present continuous tense) and connecting which I was refering to.

If you want people to think you know what you are talking about you need to learn to speak the language.

Jerry Peck
02-05-2009, 12:19 PM
Yup--Jerry --it will be confusing until you learn to read English.. Grounded is the (past tense) end result of bonding (present continuous tense) and connecting which I was referring to.

If you want people to think you know what you are talking about you need to learn to speak the language.


Yup--Roland--it will be confusing until you learn to read ... period.

That reference stated "groundED", "ground", and "groundING".

We were talking about "ground", "groundED" and "groundING", and you came up with

Are you asking about bonding the metal gate itself? Only the motor frame is required to be bonded.

I know where YOUR confusion came into play, the original poster stated: (underlining is mine)

Here's the setup:

Exterior automatic gate opener for a driveway
Wired back to panel which goes to ground
The motor is bolted to a steel frame on which the support pole is in the ground about 24"Is this sufficiently bonded?

The correct answer is: Yes, it is "groundED", it is REQUIRED to be "groundED", that is done through the "groundING" conductor, and, no, "groundED" and "bonded" are not the same thing.

You post here ...

The motor bolted to the steel frame is enough. There is actually no code requirement to bond the gate. There may be a manufacturers requirement to bond the gate. You may have to contact them..
... tried to make that connection and correction, but you had already confused yourself with your previous post.

Then you said:

Well Jerry here we go--The NEC doesn't use the term grounded in regard to the motor. It uses bonded and connected, avoiding the use of the term grounded. 250.102, 250.8, 250.110 250.112, 250.119 and 250.148. About as close as they get is calling it bonded and connected.. So the motor is (according to the NEC) "bonded" to the equipment grounding conductor. So Bonded is a more correct term according to the NEC..

Which I posted the code to show you that, yes indeed, the code does use the term "groundED" in regard to the motor.

From the 2008 NEC. (underlining and bold are mine)
- 430.242 Stationary Motors.
- - The frames of stationary motors shall be grounded under any of the following conditions:
- - - (1) Where supplied by metal-enclosed wiring
- - - (2) Where in a wet location and not isolated or guarded
- - - (3) If in a hazardous (classified) location
- - - (4) If the motor operates with any terminal at over 150 volts to ground
- - Where the frame of the motor is not grounded, it shall be permanently and effectively insulated from the ground.

Roland,

Instead of trying, fruitlessly I might add, to always try to find something wrong with what I post and actually spend your efforts to try to help, your efforts would not make you look so incompetent. But trying to say you meant one thing, when you said something else, then pointing to something I said and trying to say it makes no sense, when *you said "The NEC doesn't use the term grounded in regard to the motor." and the NEC clearly does, as I pointed out "The frames of stationary motors shall be grounded " ...


Well, the exchanges between the two of us would no longer hinder what is being done here, as I am sure most think they are.

Learn to read, learn to type, learn to read what you type, learn to read what I type - it really is that simple - I know you can do it. :rolleyes:

A.D. Miller
02-05-2009, 12:54 PM
Learn to read, learn to type, learn to read what you type, learn to read what I type - it really is that simple - I know you can do it.


Roland: I believe you have been earthed.:D

Roland Miller
02-05-2009, 12:58 PM
I was hoping for bonding:confused:

Jerry Peck
02-05-2009, 12:59 PM
I'm not into bondage. :eek: