View Full Version : Another mobile home feeder



Roland Miller
02-09-2009, 03:46 PM
I recently inspected a MH feeder. The HO used type TC cable rated for direct burial. It is #4 4 wire copper with a bare equipment ground under the outer covering. The service is 100 amps. Is this a code compliant installation??

Fred Warner
02-09-2009, 05:01 PM
I recently inspected a MH feeder. The HO used type TC cable rated for direct burial. It is #4 4 wire copper with a bare equipment ground under the outer covering. The service is 100 amps. Is this a code compliant installation??

550.33 ('05) requires 4 insulated conductors or a listed cord. Is the TC tray cable? or is it listed for mobile home assembly?

Roland Miller
02-09-2009, 05:11 PM
Fred- this is TC cable listed for direct burial all the way from the pedistal to the MH service equipment.