Michael Thomas
02-24-2009, 07:10 AM
Ran across this on a DIY board ... one more thing to think about:
Using a standard breaker as a main breaker may not provide the interrupting capacity you'll need to open should a fault occur.
Most main breakers, if not all, have a 22 kaic rating and branch breakers usually have a 10 kaic rating.
These are allowed to be used per the "2 tier system" because the 10 is being protected upstream with the 22.
I'm referring to 110.9, 110.10 and 240.89. Also, this provides some information as well http://ecatalog.squared.com/pubs/Ele...4100DB0301.pdf (http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/4100DB0301.pdf)
I would check with the POCO to see what the available fault current is so, in the event of a fault, the breaker is capable of interrupting it.
Using a standard breaker as a main breaker may not provide the interrupting capacity you'll need to open should a fault occur.
Most main breakers, if not all, have a 22 kaic rating and branch breakers usually have a 10 kaic rating.
These are allowed to be used per the "2 tier system" because the 10 is being protected upstream with the 22.
I'm referring to 110.9, 110.10 and 240.89. Also, this provides some information as well http://ecatalog.squared.com/pubs/Ele...4100DB0301.pdf (http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/4100DB0301.pdf)
I would check with the POCO to see what the available fault current is so, in the event of a fault, the breaker is capable of interrupting it.