This is borderline, would you call this out?

Thanks
Mat

Billy Stephens
02-26-2009, 06:01 PM
This is borderline, would you call this out?

Thanks
Mat
.
Is the notch wider than 1/3 the depth of the rafter? ;)
.

Ron Bibler
02-26-2009, 06:14 PM
I would. if that ever splits it could come back on you... Is that pipe up on the rafter?

Best

Ron

Brent Simmerman
02-26-2009, 08:41 PM
I agree with Ron, I would call it out.

Trent Tarter
02-26-2009, 10:33 PM
I don't believe I would call that out.

Ron Bibler
02-26-2009, 11:14 PM
I don't believe I would call that out.

Trent you can make a note: about anything. I think that its just smart to make notes on just about everything that is not perfect or if its been adjusted in some way. but thats me.

Best

Ron

mathew stouffer
02-27-2009, 09:56 AM
Thansk guys. I found a section in the code which states it is acceptable.

Glenn Duxbury
02-28-2009, 07:20 PM
Hi, Guys &

Definitely 'Butchered"...

I'd sure call it !


CHEERS

Mike Schulz
03-01-2009, 10:55 AM
Allot light around those pipes. Is the roof flashings in place.

If it was within guidlines it wouldn't go in my report.

Wayne Carlisle
03-02-2009, 02:20 PM
There are other rafters that are close enough to it AND it is within the allowed notch (your statement) Then no reason to call it out.

Richard M. Pinkerton
03-09-2009, 08:03 PM
IBC 2006- "2308.10.4.2 Notches and holes. Notching at the ends of
rafters or ceiling joists shall not exceed one-fourth the
depth. Notches in the top or bottom of the rafter or ceiling
joist shall not exceed one-sixth the depth and shall not be
located in the middle one-third of the span, except that a
notch not exceeding one-third of the depth is permitted in
the top of the rafter or ceiling joist not further from the
face of the support than the depth of the member."

Pretty much says it all.