PDA

View Full Version : outlet above h2o ???



Ryan Busch
04-04-2009, 04:55 PM
I do not think this is ok looking for info?:confused:

http://www.inspectionnews.net/home_inspection/attachment.php?attachmentid=11083&stc=1&d=1238888761

John Dirks Jr
04-04-2009, 05:55 PM
I don't think there's a problem there. It's better above the water source than below it. As it is, if a leak developes the water will drain down away from the receptacle.

If it were close by anywhere below the water source, theres always a chance that water could trickle down the cord and into the receptacle.

archivoyeur
04-04-2009, 06:55 PM
How about GFI?
Personally, I hate mixing water and electricity. I can't even use my jet tub without a nice bottle of wine first...

"Laundry and wet bars. GFCI protection is required for receptacles located within 6 feet of a laundry, utility room, or wet bar sink [210.8(A)(7), 210.52(F)]. There are no exceptions to this rule, so even a receptacle for a clothes washer must be GFCI protected if it is within 6 feet of the sink"

Branch Circuits - Applying GFCIs and AFCIs (http://ecmweb.com/mag/electric_branch_circuits_part_2/)

Fred Warner
04-04-2009, 07:11 PM
I do not think this is ok looking for info?:confused:

http://www.inspectionnews.net/home_inspection/attachment.php?attachmentid=11083&stc=1&d=1238888761

The installation you have pictured looks OK to me. (Assuming all other code provisions are met.)

Jerry Peck
04-04-2009, 07:21 PM
"Laundry and wet bars. GFCI protection is required for receptacles located within 6 feet of a laundry, utility room, or wet bar sink [210.8(A)(7), 210.52(F)]. There are no exceptions to this rule, so even a receptacle for a clothes washer must be GFCI protected if it is within 6 feet of the sink"

That is not required to be GFCI protected unless there is a sink within 6 feet, and if that receptacle is changed out to a single receptacle for laundry uses, then GFCI protection would not be required anyway.

Which is not saying that GFCI is not allowed or not a good thing to install, just that GFCI is not 'required' - that said, though, I have always recommend installing GFCI protection when water is nearby.


The installation you have pictured looks OK to me. (Assuming all other code provisions are met.)

I agree with Fred, as long a "looks OK" means "meets minimum code", installing GFCI protection would definitely make it 'look okay'. :)

ken horak
04-05-2009, 05:07 AM
Assuming that is not within 6' of a sink, in an unfinished basement, or garage it is ok as per the most recent nec code.

In the 2008 NEC all 15 and 20 amp receptacles in unfinished basements,bathrooms, garages,outdoors, crawl spaces, kitchen counter tops and anything within 6' of a sink or wet bar.
The provision for using a single outlet in place of a GFCI has been eliminated from The 2008 NEC.