View Full Version : Oh No! Another TPR Question



imported_John Smith
04-14-2009, 05:39 PM
TPR Valve and discharge pipe at about 45deg off set from plumb (plumb being vertical). All literature I have ever saw shows the TPR installed so the discharge is vertical, however after going vertical (down) I have seen many cases of 90's and pipe running horizontal and then outside or to another location.


Hey at least its going down, but it doesn't seem quite right for the TPR to angled 45 degrees?

Any referencing code or something I can use?

Jerry Peck
04-14-2009, 05:52 PM
As long as it slope down the entire distance to its termination, is not trapped, and the end is within 6" but not less than 6" of the air gap receptor or floor drain, etc., then it will be acceptable.

JB Thompson
04-14-2009, 08:06 PM
P2803.6.1

"flow by gravity"

plus all of the other stuff Jerry P. said

oh, and no "tee fittings"