30 year old house.

The door from the garage into the house by way of the laundry room is a typical interior hollow core door with galvanized on the garage side. Hard to believe it would last very long in a fire, but I'm not sure how to evaluate it.

The 2006 IRC says solid wood, or steel, or "20 minute fire-rated".

I recommended replacement with a "proper fire-rated door", but mainly just because of a gut feeling, which I'd rather not rely on.

Jerry Peck
04-16-2009, 07:21 PM
Arrrrgggg ... :D

(the title)

It *IS NOT* a "fire door".


The door from the garage into the house by way of the laundry room is a typical interior hollow core door with galvanized on the garage side. Hard to believe it would last very long in a fire, but I'm not sure how to evaluate it.

The 2006 IRC says solid wood, or steel, or "20 minute fire-rated".

Why did you not just recommend what the code says, instead of recommending something the code does not say? :confused:


I recommended replacement with a "proper fire-rated door",

You should have simply said 'replace with a door suitable for this use, such as: solid wood door not less than 1-3/8" thick; honeycomb steel door; or a 20 minute fire-rated door'

R309.1 Opening protection. Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.

:confused:


:)

Tom Rees
04-17-2009, 06:53 AM
Jerry, What makes a door a "20 minute fire door" could the galvanized on garage side make it this? Is 20 minute rating stamped on door somewhere and what if it's been removed? Just picking your brain.:D

John Dirks Jr
04-17-2009, 07:13 AM
Just for the record, and I'm sure most of you already know this, these fire doors also need a self closing mechinism. Usually, it's spring loaded hinges.

Scott Patterson
04-17-2009, 07:14 AM
Jerry, What makes a door a "20 minute fire door" could the galvanized on garage side make it this? Is 20 minute rating stamped on door somewhere and what if it's been removed? Just picking your brain.:D

A solid wood 1 3/8" thick door.

OR

A door with a label on it.

If the label is missing then you should say that you can not confirm if the door is fire rated for 20 minutes.

Scott Patterson
04-17-2009, 07:17 AM
Just for the record, and I'm sure most of you already know this, these fire doors also need a self closing mechinism. Usually, it's spring loaded hinges.

Nope, no longer a requirement unless your local AHJ requires it.

Wayne Carlisle
04-17-2009, 07:23 AM
Adding a little more to what Scott said. The label should also be on the frame because these types of doors (20 minute rated) are tested as a unit and must be labeled as such.

Jerry Peck
04-17-2009, 09:23 AM
Jerry, What makes a door a "20 minute fire door" could the galvanized on garage side make it this? Is 20 minute rating stamped on door somewhere and what if it's been removed? Just picking your brain.:D

Having been tested, listed, and labeled as a 20 minute fire-rated door. The part of that is "labeled", if it is not "labeled" it is not a 20 minute fire-rated door.

Jerry Peck
04-17-2009, 09:27 AM
Just for the record, and I'm sure most of you already know this, these fire doors also need a self closing mechinism. Usually, it's spring loaded hinges.

John, John, John, :)

Are you not reading the above posts? :D

"these fire doors"?????

They are not "fire door", how many times does that need to be said?

If the door is labeled as a 20 minute fire-rated door, then, yes, THAT DOOR will have self-closing hinges as it is rated as an assembly of the door AND its frame and hardware.

However, none of the other options are required to be self-closing.

Like with "subpanel", "fire door" needs to be dropped from home inspector speak and home inspection reports, unless you are actually in a location which requires a fire-rated wall assembly and a fire-rated door, in which case then and only then is that a "fire door", more accurately a "fire-rated door".

Jerry Peck
04-17-2009, 09:31 AM
Jerry, What makes a door a "20 minute fire door" could the galvanized on garage side make it this? Is 20 minute rating stamped on door somewhere and what if it's been removed? Just picking your brain.:D


A solid wood 1 3/8" thick door.

OR

NOPE!


A door with a label on it.

Yep.


If the label is missing then you should say that you can not confirm if the door is fire rated for 20 minutes.

Which is why a solid wood 1-3/8" thick door is not a 20 minute rated door - it is not labeled, and if it is labeled, then instead of referring to it as a solid wood 1-3/8" think door you would refer to it as a 20 minute labeled door. ;)

Jerry Peck
04-17-2009, 09:32 AM
The label should also be on the frame because these types of doors (20 minute rated) are tested as a unit and must be labeled as such.


If it is a 20 minute fire-rated door, yes, it will be labeled and yes, it is tested as a unit, and it will have self-closing hinges.

John Arnold
04-17-2009, 11:24 AM
Whaaack!

Thank you, Sir/JP! May I have another?

Whaack!

(repeat)

I feel like Bart Simpson at the black board: It is NOT a "fire door". It is NOT a "fire door". It is NOT a "fire door". It is NOT a "fire door".

I think I've almost got it...

It is NOT a "fire door". It is NOT a "fire door". It is NOT a "fire door"...

Jerry Peck
04-17-2009, 11:36 AM
..:D ..

Tom Rees
04-17-2009, 12:05 PM
Jerry, It's not a subpanel it's a__________?:D

Jerry Peck
04-17-2009, 12:09 PM
Jerry, It's not a subpanel it's a__________?:D

... it is "a panel", or a "distribution panel", or a "loadcenter", or even a "remote panel", but it is simply just a "panel". :)