View Full Version : AFCI Exception



Ken Amelin
04-21-2009, 10:00 AM
I inspected a home that had new service equipment.

I noticed that there were no AFCI breakers in the panel. I questioned this and the electrician told me that an amendment was made to the electrical code that states - AFCI breakers are not required for a service upgrade??

Can anyone confirm and provide the language for this exception?
Thanx

Jerry Peck
04-21-2009, 10:41 AM
There is no exception because there is no requirement.

Replacing the service has nothing to do with the circuits needing AFCI protection.

*Installing new circuits* would be different, were any "new" circuits installed? If so, *those* new circuits would require AFCI protection.

Bill Kriegh
04-23-2009, 04:59 AM
There does appear to be a violation of the requirement for the cables to be secured within 12" of the panel.