PDA

View Full Version : 14 gauge wire pigtail off a 20 amp. circuit



Robert Mattison
08-07-2009, 03:31 PM
From time to time I run across wiring, where the circuit is wired with 12-2 or 12-3 and where more than one cable enters a single outlet box.

All there wires are group together, BLACK/WHITE/BARE COPPER into a single pigtail that will attach to a receptacle, general its a 15 amp rated
duplex receptacles. SO THE LEADS ATTACH TO THIS DUPLEX RECEPTACLE
ARE PROTECTED BY A S/P 20 AMPERE CIRCUIT BREAKER BACK AT THE HOUSE ELECTRICAL PANEL.

My stand is this not acceptable, and must be change to #12 wire.

But I talk to the electricians in my area, the old timers say its okay.
The younger ones agree me. Follow inspectors, what are your thoughts?

Jerry Peck
08-07-2009, 05:00 PM
All there wires are group together, BLACK/WHITE/BARE COPPER into a single pigtail ...

Robert,

I'm not following that: if the black/white/bare ground are all tied together in a single pigtail under a single wire nut, that would create both a dead short and a dead ground fault, either and both of which would trip the breaker.

Would you give a different description of what you are talking about so I can follow it?

Robert Mattison
08-07-2009, 06:28 PM
Yes Jerry, bad description on my part. The black/HOT is pigtail to black.
White/ground is pigtail to white, Bare copper/grounding conductors is pig-
tail to same/green insulated or bare copper. Now the box has been made-
up with three leads extending from it.

One lead is HOT, Black Conductor, One lead is Ground, White Conductor.
Third lead is bare copper - grounding conductor.

The thing about all three leads, is their usually #14 not #12.

My thing is you should not mix conductor size. By attaching #14 gauge
wires as pigtails, the 20 amp. breaker should be change to 15 amp. or
all pigtails should be change to #12 gauge wire, if you want to stay with
the 20 amp. breaker. Well that my story.

Here the 2nd. part of my story: on switches, I find #14 gauge on the load
side of the switch going directly to a fix light fixture/luminaire. But the
feed side of the switch is coming at #12 fuse at 20 amperes.

Thanks for your interest. /S/ Robert

Brandon Whitmore
08-07-2009, 06:34 PM
Hi Robert,

Jerry has a much better understanding of the NEC that I do, but I believe that you are correct. Unless the wires are protected by a 15 amp breaker, then 14 gauge wire is not allowed.

Jerry Peck
08-07-2009, 07:53 PM
My thing is you should not mix conductor size. By attaching #14 gauge wires as pigtails, the 20 amp. breaker should be change to 15 amp. or all pigtails should be change to #12 gauge wire, if you want to stay with the 20 amp. breaker. Well that my story.

I don't recall anything which would allow those #14 pigtails to be installed on #12 circuits which are protected by 20 amp breakers.


Here the 2nd. part of my story: on switches, I find #14 gauge on the load side of the switch going directly to a fix light fixture/luminaire. But the feed side of the switch is coming at #12 fuse at 20 amperes.

That would be the switch leg, and should also be #12 if on a 20 amp circuit.

Remember, the breaker is not there to protect the equipment (such as the light fixture) it is there to protect the circuit wiring.

Thus, the switch leg would be a no brainer, however, if you have more than one receptacle outlet on a 20 amp circuit, the receptacle outlets are allowed to be 15 amp rated, so in that sense, and with the pigtail being entirely in the box with the 15 amp rated receptacle, there really would not be much difference whether the receptacle burned up or the pigtail burned up ... however ... as I said, I do not recall anything allowing that, I was just explaining a thought process which may have lead to that being done - or maybe they just did not think at all.

Of course, if the circuit is a 20 amp circuit and *is not to locations which require a 20 amp circuit*, then changing to a 15 amp breaker is easy to do, and if nothing starts tripping the breaker, no harm no foul, but if the breaker starts tripping, then all the pigtails would need to be changed to #12 20 amp rated.

Just some thoughts on the issue.

John Steinke
08-10-2009, 12:30 PM
The NEC has a variety of "tap rules" that could, concievably be used to allow using a #14 wire to 'tap' a receptacle off a 20 amp circuit. There used to be - perhaps as recently as the 60's - some debate on this point.

Debate became moot, however, when the NEC specifically forbade this practice.

So, why is it still done? Simply because the 'push in' connections on receptacles will not accept #12 wire, and there are several circuits that are required to be 20 amp circuits.

Robert Mattison
08-10-2009, 03:58 PM
Insteresting point of view.:) .

Are you saying only gauge 14 can be use with the non-comericial type
receptacles/switches.

Case in point, I have in my collection, one 3-way Levition Brand switch.
It is clearly spell out on the back, "#12 & #14 Solid Wire Only". So I tested it with both #12 and #14 wire both seen to fit. But this used
Leviton fail the test on holding the wire. I could easly pull out either
size guage wire.

How ever another brand, P & S, LIST ONLY SOLID #14 for push in quick
connect, and clearly the slot looks smaller than on the Leviton Brand.

In both test I found that once the wire was push in, and some type of
chinese finger grab. It was not a tight connection, the wire, both gauges
could easly be twisted around while connected. "I WOULD NOT EVER
TRUST THIS TYPE OF CONNECTION. U.L. BE DAMN.

Case in point, a previously inspection before the sell of trailer, 50% of
the receptacle, that were made up using only the push-in connection
had fail.:cool:

Jim Port
08-10-2009, 05:01 PM
Robert,

Along with the labeling for use with only 14 ga. conductors the NEC also specifies that the backstabs can only be used with 14 ga. conductors.

Robert Mattison
08-10-2009, 05:13 PM
Jim P. thanks for the Heads Up. I miss that.

Jim Port
08-10-2009, 05:20 PM
You are very welcome.