So....I'm doing an inspection not too long ago and ran across this kitchen GFCI with a sticky-tricky neutral. Shot a little video...check it out and you electrician-types (check your shorts! :D ) give me your best analysis! And no..... 'uh...sumthin's stickin!' doesn't qualify as an answer....Ted! (Did I actually say Ted's name out loud or did I just think it!?)

Ready...set...YouTube - GFCI with tricky neutral leg (http://www.youtube.com/watch?v=Qdolwa5bo-A)

Michael Thomas
08-10-2009, 02:54 AM
Humm... time to read up on my camera's video features.

Rick Cantrell
08-10-2009, 03:46 AM
Contacts in relay of GFCI sticking.
Replace GFCI

Jerry Peck
08-10-2009, 07:41 AM
A good argument for testing with a tester, not with the GFCI button.


Fritz,

Trying to figure out how you got from Point A (what was shown in that video) and Point B (your statement above).

The GFCI is defective and that would have shown up either way.

The proper way to test GFCI protected receptacles is to check the receptacles with a good circuit tester (those three light night lights do not fall under "a good circuit tester") to verify proper and correct wiring of the receptacles, push the Test button on the GFCI, then recheck the receptacles to make sure they all are now off (which is the only way to know that it was indeed properly GFCI protected).

Yes, you "can" test the GFCI protection with a GFCI tester from EACH receptacle, but the test is the same: plug in the tester to make sure the receptacle is wired correctly, push the Test button (this time on the GFCI tester) to make sure power shuts off, go to the GFCI device and Reset the GFCI device.

Thus, I am not following how you got to your Point B above???

The person doing the test in the video did the same thing - tested the receptacles first and found a problem, tested the GFCI and then reset it, and the problem went away, which means the GFCI is defective.

I think all HIs use the same procedure for testing GFCI: test receptacles, trip GFCI, test receptacles, reset GFCI, and most probably do as I did and re-test the receptacles one last time after resetting the GFCI to make sure they are all back on.

Richard Abrams
08-10-2009, 10:53 AM
Since none of the recps are wired correctly I think you have a reversed neutral in some junction box somewhere. Starting at the closet recp to panel remove recp and check wires and then continue. May require total rewire.

Rick Cantrell
08-10-2009, 11:15 AM
Since none of the recps are wired correctly I think you have a reversed neutral in some junction box somewhere. Starting at the closet recp to panel remove recp and check wires and then continue. May require total rewire.

Why do you say that?

Richard Abrams
08-10-2009, 11:23 AM
When I watched the video all of the recps he tested showed open neutral or reversed ground buttons lite up on the tester.

Jerry Peck
08-10-2009, 06:06 PM
Jerry, how would you know it is defective without the tester, whatever quality? When you push the test button, it trips, just like a non-defective GFCI.

By doing what I said.

Did you read what I said on how to test the GFCI protected receptacles? :confused:

Jerry Peck
08-10-2009, 09:55 PM
if all you are going by is the test button, everything looks OK.


*IF* all you are doing is pushing the test button then you are not checking the GFCI protected receptacles properly to start with.

Matthew Barnicle
08-11-2009, 03:50 AM
I would report: "GFCI receptacle(s) in kitchen not functioning properly/intermittent deficiency. Recommend review GFCI system(s) and repair as needed by licensed electrical contractor." - DONE

Speedy Petey
08-11-2009, 04:04 AM
When I watched the video all of the recps he tested showed open neutral or reversed ground buttons lite up on the tester.Not all testers are the same. With my Ideal plug-in the two outside lights mean correct wiring. On the OP's tester the two right lights mean correct.

This is a bad GFI. Plain and simple.

Glenn Curtis
08-12-2009, 03:42 PM
I would report: "GFCI receptacle(s) in kitchen not functioning properly/intermittent deficiency. Recommend review GFCI system(s) and repair as needed by licensed electrical contractor." - DONE

I don't know about the rest of my brother H.I.'s, but it always grinds-my-bacon when I make a report call-out similar to what Matthew stated above, and the electrician shows up and checks/tests the GFCI-protected outlet(s) and then says something about the 'stupid-inspector' and 'everything is OK...' and the client or homeowner calls me back to gripe....and then I pull out my little video (which they have NOT seen yet, because it's a part of my 'Work File' which my clients DO NOT see, just because of situations like this one) and then it's my turn to practice the 'Last-Man-In' scenario on the electrician who just 'dissed' me! Whew!

Doing 250-350 digital photos and 20-40 video's really adds substantial time to each inspection...but in this day-and-age of 'everything-electronics' I figure it's a cheap 'Expert-Witness' that I invest in every day...a little at a time. Just like my Martial Arts. A little 'practice' every day...just-in-case! :cool:

If any of youse' guys are coming to the COA-'Inspector Stimulus Conference' at the end of September, I'll be a presenter on Home Inspector Risk-Management, Blackbelt Style! I'd be proud to have any of youse' guys stop in and say Hi, and then sit-down and rest a spell while I do 'my-thing'! Hopefully it will be enjoyable for all and we'll leave a little better for the experience.

Speedy Petey
08-12-2009, 05:38 PM
I don't know about the rest of my brother H.I.'s, but it always grinds-my-bacon when I make a report call-out similar to what Matthew stated above, and the electrician shows up and checks/tests the GFCI-protected outlet(s) and then says something about the 'stupid-inspector' and 'everything is OK...' and the client or homeowner calls me back to gripe....So how could this happen in this case? A case where the problem is consistent and repeatable?

I doubt you'd get any flak about this one. :cool:

Jerry Peck
08-12-2009, 05:46 PM
So how could this happen in this case? A case where the problem is consistent and repeatable?

I doubt you'd get any flak about this one. :cool:


Peter,

It is not "consistent and repeatable".

It apparently started off wrong, tested and reset correctly, then after trying it a few more times it reset wrong again.

I used to have the same thing happen and the GFCI would reset "reverse polarity" every so often, not all the time. I had manufacturer's tell me that was impossible, until I met one at a seminar one day and showed him.

I have had similar things happen and the electrician (or other tradesperson) would come in, test it, reset it, and it would work properly ... THAT time ... but they would not sit there and play with it to see if it always worked properly. On occasion, new homes usually, I would go back with my client, the builder, and the electrician and play with it a few times and ... WHOA! LOOKEE THERE! It just did what I said it was doing. :D