View Full Version : Neutrals and grounds
Ryan Stouffer
10-01-2009, 11:27 AM
Nice panel
Ryan Stouffer
10-01-2009, 12:56 PM
New post
Speedy Petey
10-01-2009, 12:58 PM
They occupy the same bar in the service equipment or main panel.
Jim Port
10-01-2009, 02:34 PM
No offense meant, but shouldn't common topics like this be covered in the training courses? Isn't there any requirement to shadow an experienced inspector before doing this on your own?
I commend you for asking questions as that is how we all learn. But how good can the inspection be when the common topics still need to be covered?
John Arnold
10-01-2009, 02:51 PM
Couple of black conductors there need to be properly marked as grounded/neutral conductors.
Speedy Petey
10-01-2009, 03:28 PM
Couple of black conductors there need to be properly marked as grounded/neutral conductors.I see one grounded conductor and it is white. :)
I don't see a grounded conductor for that 100A breaker on the left. :confused:
There is no requirement that a grounding electrode conductor or bonding conductor be green. :cool:
Gunnar Alquist
10-01-2009, 03:40 PM
Nice panel
I am not sure why you posted this. Are you looking for feedback on something in particular?
John Arnold
10-01-2009, 04:13 PM
I am not sure why you posted this. Are you looking for feedback on something in particular?
Gunnar - For some reason he deleted his question about whether neutrals and grounds needed to be on the same bar in the service equipment.
Speedy Petey
10-01-2009, 04:27 PM
Gunnar - For some reason he deleted his question about whether neutrals and grounds needed to be on the same bar in the service equipment.
Wow. I just noticed that.
WHY do original posters do that???? Makes the whole thread useless.:(
Gunnar Alquist
10-01-2009, 04:59 PM
Gunnar - For some reason he deleted his question about whether neutrals and grounds needed to be on the same bar in the service equipment.
John,
Thanks. I thought I was being EXTRA dense today. Good to know that I am just regular dense. :cool:
Robert Mattison
10-02-2009, 04:20 PM
If the wires are feed in thru conduit, I believe you would have to duct seal
around all the wires to seal the conduit openning. :cool:
Speedy Petey
10-02-2009, 04:43 PM
If the wires are feed in thru conduit, I believe you would have to duct seal
around all the wires to seal the conduit conduit openning. :cool:I have never heard of such a requirement.
Jerry Peck
10-02-2009, 05:04 PM
I have never heard of such a requirement.
Peter,
I believe he is referring to sealing required for raceways which go down into the ground.
Robert Mattison
10-03-2009, 02:50 AM
My reply in my last post comes from, the NEC 2008 edition:
300.5(G) Raceway Seals
300.7 Raceway Exposed to Different Temperatures :cool:
Michael Thomas
10-06-2009, 06:45 PM
Borrowing the thread for a moment, for today's jewel of a neutral.... I now return you to your regularly scheduled programming....
Michael Thomas
10-07-2009, 03:37 AM
BTW, what section of the NEC governs the splicing of SECs?
Jerry Peck
10-08-2009, 05:09 PM
BTW, what section of the NEC governs the splicing of SECs?
- 230.46 Spliced Conductors.
- - Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
Joe Klampfer
10-28-2009, 07:32 AM
- 230.46 Spliced Conductors.
- - Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
Jerry, Since I'm a little north of you, I'm not familiar with the NEC but doesn't that sentance refer to splicing of the actual feeder cable (ie: extending it) and not splicing the branch circuit wires to the feeder (as in lack of neutral bar) ?
Also, does the NEC allow all the branch circuit wiring to enter and pass through the main-switch compartment ?
Just curious.
Jerry Peck
10-28-2009, 04:13 PM
BTW, what section of the NEC governs the splicing of SECs?
- 230.46 Spliced Conductors.
- - Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
Jerry, Since I'm a little north of you, I'm not familiar with the NEC but doesn't that sentance refer to splicing of the actual feeder cable (ie: extending it) and not splicing the branch circuit wires to the feeder (as in lack of neutral bar) ?
Joe,
The question was about "service entrance conductors", thus the reference to splices for service entrance conductors, not feeders or branch circuits.
Also, does the NEC allow all the branch circuit wiring to enter and pass through the main-switch compartment ?
No. I believe you are referring to using the panel as a "raceway", i.e., "does the NEC allow all the branch circuit wiring to enter and pass through", and all the conductors in the panel are to be terminated in that panel, either at the grounding terminals, neutral terminals, or at an overcurrent device. This means that "passing through" is not allowed.
Joe Klampfer
10-28-2009, 05:34 PM
Sorry Jerry, I thought we were both talking about the photos in post # 15 above.