View Full Version : A/C Condensate Drain Connected To Waste Piping



Bruce Breedlove
10-14-2009, 06:04 PM
Anything wrong with connecting the A/C condensate drain directly to the waste piping as seen in the attached photos?

Bruce Breedlove
10-14-2009, 06:08 PM
delete

Jim Luttrall
10-14-2009, 06:17 PM
Yep, it must be an indirect connection. You don't want the nasties from the sewer from the sewer to migrate to the air stream.

Bruce Breedlove
10-14-2009, 06:20 PM
Jim,

Wouldn't the trap stop the sewer gasses from flowing up the pipe?

Jim Luttrall
10-14-2009, 06:28 PM
It's not just gases, think bacteria and legionnaire's disease.
Plus that trap is not vented, is a running trap, and will likely dry out during the off season.

Bruce Breedlove
10-14-2009, 06:59 PM
OK, thanks. Time to send out a revised report.

Jerry Peck
10-14-2009, 07:51 PM
Wouldn't the trap stop the sewer gasses from flowing up the pipe?

Bruce,

That trap is not stopping anything.

That is a site built "running trap" and running traps are prohibited. Also looks like it might be longer than 4 feet and PVC is required to be supported every 4 feet. Plus, you would want a support at that 90 change from vertical to horizontal to 90 degreed horizontal, otherwise the fittings could break.

Brad Deal
10-14-2009, 10:10 PM
Bruce,

This is called a "cross connection." If the sewer line backs up, sewer water will be forced into the condensate drain and into the condensate pan. Black water is now in direct contact with the air we breath, vented throughout the living space. This is akin to an overflowed toilet inside the HVAC system.

This is a health safety hazard.

Brad Deal

Bruce Breedlove
10-14-2009, 10:31 PM
Message received and understood. Client has been sent a revised report.

Thanks for the assistance and education.