View Full Version : Blade Fuse Size



Sam Morris
03-06-2010, 07:31 PM
This might be a stupid question but, here goes. Is this blade fuse a 100 AMP fuse or a 200 Amp. Does the (2) 100 AMP fuses make a 200 AMP system?? Thanks

Jim Luttrall
03-06-2010, 07:38 PM
100 amp, 230Volt assuming that is a 230 volt pull out fuse block.
It is twice the voltage and power but the amperage is still limited to 100 amps.

ken horak
03-07-2010, 07:39 AM
Those fuses are 250 volt 100 amp.
Until you get into medium and high voltage work , Fuses for AC come in 2 voltage ratings. They are 600 volt and 250 volt.
250 volt are to be used on anything under 250 volts ( 240 , 208 volts)
600 volt are to be used on anything OVER 250 volts and UNDER 600 volts.
( 480 , 277 volt) (This is something to keep in mind for those of you who do commercial inspections were there is 480 volt electrical systems)

NO the 2 -100 amp fuses do not make a 200 amp system, it is 100 amps at 240 volt.
Think of that pull out as a 2 pole circuit breaker. In this case a 2 pole 100 amp circuit breaker. It's only good for 100 amps.

Jerry Peck
03-07-2010, 07:36 PM
And while you are at it ... keep in mind that many insurance companies WILL NOT INSURE a house which has fuses panels in it, meaning that the panel will need to be replaced just to be able to get insurance.