When an electronic damper has been disconnected, is it acceptable to leave it in place?

wayne soper
03-30-2010, 08:21 AM
As a home inspector, No, not allowed. You (we) cannot allow ourselves to be put in a position where we are determining that a mechanical device that is no longer operable will not cause someone to die.
What if the kids playing in the basement whack it with a hockey puck and it causes the damper to close.
call the defects, there are more brokers

David Bell
03-30-2010, 04:00 PM
If it is a zone damper it can be left in place as long as it is locked in the open position by some means. If it is a vent damper it cannot.

Jerry Peck
03-30-2010, 05:40 PM
If it is a zone damper it can be left in place as long as it is locked in the open position by some means.


Not necessarily.

Not unless you know the system as since been modified to do without the damper, otherwise it is a requirement for that system to operate as the system was intended to operate and the abandoned damper may well simply be a result of 'someone not wanting or being able to pay to have it fixed'.

The home inspector is not in a position to know, so it should be written up for repair or replacement.

David Bell
03-30-2010, 05:51 PM
Not necessarily.

Not unless you know the system as since been modified to do without the damper, otherwise it is a requirement for that system to operate as the system was intended to operate and the abandoned damper may well simply be a result of 'someone not wanting or being able to pay to have it fixed'.

The home inspector is not in a position to know, so it should be written up for repair or replacement.

The question wasn't if it should be written up, it was can it be left in place.

Jerry Peck
03-30-2010, 05:54 PM
The question wasn't if it should be written up, it was can it be left in place.

That was the question, yes, but I suspect the question was leading to - then should it be written up.

I could be wrong, I have been many times before.

Bob Harper
03-30-2010, 07:44 PM
An electric vent damper serves to reduce stack losses, which affects the appliance's AFUE rating and maintains stack temps, which improves draft. The damper should default into the full oepn position. It has a microswitch that must close in order for the gas train to complete the sequence and fire. If the safety circuit is open, no burner. These dampers do have a manual override switch, which leaves the damper wired in and maintains the safety circuit--the circuit just remains closed all the time.

In order to disconnect a vent damper, you would have to disconnect the safety circuit. Tampering with a primary safety control is negligence and a code violation.

The question is, why was this damper bypassed? Venting problems? Was it sticking open failing to complete the circuit? This is a huge red flag that must be investigated.

Bob

Rod Butler
03-31-2010, 07:26 AM
IMO Vent dampers have always been a bad idea. Just a quick and cheap fix to a larger problem. The system will operate fine without it in place. I would recommend it be fixed or removed completely.