View Full Version : exposed cable run



Jon mackay
03-31-2010, 07:53 AM
Is extra protection required here?

Ron Bibler
03-31-2010, 07:55 AM
Nice hand rail...:D They should have ran it with the stairs:eek:

Best

Ron

brian schmitt
03-31-2010, 09:09 AM
Is extra protection required here?
no! just your usual protection:D

JD Weekley
04-12-2010, 07:44 PM
Well, I don't think that's Mike Holmes approved....

Trent Tarter
04-12-2010, 08:47 PM
The cable should be repalced with conduit or re-routed through wall cavity.

Jim Port
04-13-2010, 05:57 AM
334.15 Exposed Work. In exposed work, except as provided
in 300.11(A), the cable shall be installed as specified
in 334.15(A) through (C).

(A) To Follow Surface. The cable shall closely follow the
surface of the building finish or of running boards.

(B) Protection from Physical Damage. The cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC rigid nonmetallic conduit, or

other approved means. Where passing through a floor, the
cable shall be enclosed in rigid metal conduit, intermediate
metal conduit, electrical metallic tubing, Schedule 80 PVC
rigid nonmetallic conduit, or other approved means extending
at least 150 mm (6 in.) above the floor.

Looks like (A) has been followed. Physical protection is a judgement call, but, IMO the cable could be possibly damaged by a vacuum.

John Kogel
04-13-2010, 07:53 AM
Anywhere a dog can chew on it should have protection.

But like Jim says, it's a judgement call and the code leaves it up to "where necessary".

Robert Hronek
04-13-2010, 08:50 AM
it there to hang socks for drying