View Full Version : Messy electrical



mathew stouffer
04-05-2010, 08:09 PM
Do you include this in your reporting. Also is Romex permitted to be run along supply ducts.

mike huntzinger
04-05-2010, 10:01 PM
can you explain when this is located, i can see the plumbing can be damaged and should be behind sheetrock so should any romex wires

Bob Knauff
04-05-2010, 10:30 PM
Do you include this in your reporting.

Absolutely. Electrical wiring unsupported and subject to abrasion and damage, PARTICULARLY where it contacts the edge of the metal duct, creates fire and shock hazard.



Also is Romex permitted to be run along supply ducts.

Yes, as long as it is not secured to them.

mathew stouffer
04-06-2010, 05:34 AM
This is in the mechanical room, house was built in 02.

dana1028
04-11-2010, 12:47 PM
Yes, as long as it is not secured to them.

Would you be kind enough to support that statement with a code section?

Jerry Peck
04-11-2010, 03:02 PM
Yes, as long as it is not secured to them.


Would you be kind enough to support that statement with a code section?


Dana,

Which part?

You mean screwing the NM cable straps to metal duct or flex duct?