View Full Version : Furnace vent initial rise
Jon mackay
04-21-2010, 12:57 PM
I know that water heaters must have an 18" vertical rise befor the first transition.
Is there a rule for gas furnaces?
Michael Thomas
04-21-2010, 03:50 PM
I'm not aware of a 18" requirement for any gas appliance.
This questions comes up here often, this is likely the most useful (if somewhat ... err.. contentious) iteration, see the second version of Jerry Peck's .pdf, near the middle of the thread.
http://www.inspectionnews.net/home_inspection/heating-ventilation-air-conditioning-hvac-home-inspection-commercial-inspection/12609-combustable-exhaust-slope.html
David Bell
04-21-2010, 04:49 PM
Most gas water heaters I have seen with draft hoods have a 6" requirement before any change in direction.
Jerry Peck
04-21-2010, 06:44 PM
Most gas water heaters I have seen with draft hoods have a 6" requirement before any change in direction.
!2 inches.
Show us where it only requires 6 inches.
David Bell
04-22-2010, 04:54 AM
Here is an example
Jerry Peck
04-22-2010, 06:22 PM
Here is an example
Thank you,
Q. Now, however, when you take the code's connector rise chart minimum of 1 foot and try to match that with that manufacturer's drawing (do you know how old that is?) what do you end up with?
A. The most restrictive shall apply. (From the codes.)
David Bell
04-22-2010, 06:35 PM
Are those not B-Vent requirements? Show me single wall pipe requirements.
Ron Bibler
04-22-2010, 06:53 PM
I see this form time to time.
Best
Ron
Jerry Peck
04-22-2010, 07:00 PM
Are those not B-Vent requirements? Show me single wall pipe requirements.
First, go back and review the drawing you posted. :rolleyes: