05-06-2010, 06:54 PM
These landings were outside secodary doors and the door swing to the inside of the home. The step down is about 9 inches. Is this acceptable? Forgot to measure the dimensions of the landing.:mad:

Rick Cantrell
05-06-2010, 06:59 PM
"These landings were outside secodary doors and the door swing to the inside of the home. The step down is about 9 inches. Is this acceptable? Forgot to measure the dimensions of the landing"

Not at 9"
Not with the broken uneven landings
and only if the landings are at least as wide as the door x 36" deep.

Jerry Peck
05-06-2010, 07:01 PM
Nope and nope.

(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel - looks like a 3' wide door, which means the landings would be square or deeper than they are wide.)

The uneven stone is another problem.

mathew stouffer
05-06-2010, 07:05 PM
Crap I will have to go measure, they are 36 inches in width but not sure the depth. So 9 inches will not work, has to be 7 3/4.

Jerry Peck
05-06-2010, 07:08 PM
Crap I will have to go measure, they are 36 inches in width but not sure the depth.


Why do you need to go measure their depth?

You just said they are 36" wide, and you KNOW they are not as deep as they are wide, therefore you KNOW they are less than 36" deep. :)

mathew stouffer
05-06-2010, 07:09 PM
Wow that was fast. I don't know, can you tell the depth from the photo.

Billy Stephens
05-06-2010, 07:16 PM
.

These landings were outside secodary doors and the door swing to the inside of the home. The step down is about 9 inches. Is this acceptable? Forgot to measure the dimensions of the landing.:mad:
.
7 3/4 is the maximum height down. @ link under threshold.
.
International Code Requirements for Windows & Doors | Window & Door (http://www.windowanddoor.com/article/codes-standards/international-code-requirements-windows-doors)
.

Billy Stephens
05-06-2010, 07:21 PM
.

Wow that was fast. I don't know, can you tell the depth from the photo.
.
One Way.
.
.

Brandon Whitmore
05-06-2010, 08:19 PM
(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel

The "landing" is just a tread if it's not the primary access door, is it not (R311.4.3 exception 1)?
But yes, there's plenty of other reasons to write them up either way.

Billy Stephens
05-06-2010, 08:34 PM
.
The "landing" is just a tread if it's not the primary access door, is it not (R311.4.3 exception 1)?
But yes, there's plenty of other reasons to write them up either way.
.
That's the way I'm reading it.

mathew stouffer
05-06-2010, 08:58 PM
so the way I am reading this, these doors do not require a landing?

Billy Stephens
05-06-2010, 09:04 PM
.
so the way I am reading this, these doors do not require a landing?
.
Only if they are not Primary Access Doors.
.

mathew stouffer
05-06-2010, 09:09 PM
They are just living room doors which exit into the back yard. So I would have to say no. A primary would be the front door or garage man door.

Brandon Whitmore
05-06-2010, 09:26 PM
A garage man door is not a primary door.

Billy Stephens
05-06-2010, 09:28 PM
.
A garage man door is not a primary door.
.
Correct http://www.staircraft.com/R311&R312%20of%20the%2006%20IRC.pdf
.

Brandon Whitmore
05-06-2010, 09:35 PM
Might as well add this one to the list:

http://www.stairways.org/pdf/2006%20Stair%20IRC%20SCREEN.pdf

Rick Cantrell
05-07-2010, 04:19 AM
Brandon is correct. it is not required to have a landing.
However, without a landing, the 2 risers need to be the same height.
With a landing, the risers can be different heights.
Either way, still needs to be a relatively smooth surface though.

Jerry Peck
05-07-2010, 02:42 PM
The "landing" is just a tread if it's not the primary access door, is it not (R311.4.3 exception 1)?
But yes, there's plenty of other reasons to write them up either way.


That's the way I'm reading it.


so the way I am reading this, these doors do not require a landing?


Only if they are not Primary Access Doors.


Yall :) need to read the entire thing and understand that exception 1 does not allow for a riser greater than 7-3/4", nor does it allow for risers which are not within 3/8" of each other.

Look at those photos (and read the first post) and you will see, especially in the second photo, that the risers are not within the maximum 7-3/4" nor are the risers within 3/8" of each other.

Thus that exception is not applicable.

Billy Stephens
05-07-2010, 03:21 PM
.
7 3/4 is the maximum height down. @ link under threshold.
.
International Code Requirements for Windows & Doors | Window & Door (http://www.windowanddoor.com/article/codes-standards/international-code-requirements-windows-doors)
.


Yall :) need to read the entire thing and understand that exception 1 does not allow for a riser greater than 7-3/4", nor does it allow for risers which are not within 3/8" of each other.

Look at those photos (and read the first post) and you will see, especially in the second photo, that the risers are not within the maximum 7-3/4" nor are the risers within 3/8" of each other.

Thus that exception is not applicable.
.
Read ? :D
.

Jerry Peck
05-07-2010, 03:58 PM
.
Read ? :D
.


Billy,

I have no idea what you are trying to point out??? :confused:

That the 7-3/4" DOES NOT apply?

That the 3/8" DOES NOT apply?

:confused:

Billy Stephens
05-07-2010, 05:36 PM
These landings were outside secodary doors and the door swing to the inside of the home. The step down is about 9 inches. Is this acceptable? Forgot to measure the dimensions of the landing.:mad:


.
7 3/4 is the maximum height down. @ link under threshold.
.
International Code Requirements for Windows & Doors | Window & Door (http://www.windowanddoor.com/article/codes-standards/international-code-requirements-windows-doors)
.


Billy,

I have no idea what you are trying to point out??? :confused:

That the 7-3/4" DOES NOT apply?

That the 3/8" DOES NOT apply?

:confused:
.
OP Stated The Step Down was about 9 inches.

I responded that 7 3/4 was the Maximum Step Down. ( with a Code Reference )
thus needs repaired or replaced,

The Two Steps Down ( or could be three after repaired ) Does apply and would have to be part of this correction.

As long as the Threads are correct the Width of the " Landing" is not an Issue.
.

Jerry Peck
05-07-2010, 06:18 PM
As long as the Threads are correct the Width of the " Landing" is not an Issue.


You mean as long as the risers are correct the depth of the landing is not an issue?

Billy Stephens
05-07-2010, 06:53 PM
.
You mean as long as the risers are correct the depth of the landing is not an issue?

Yes Risers.


.

Jerry Peck
05-07-2010, 07:11 PM
You mean as long as the risers are correct the depth of the landing is not an issue?


Yes Risers.


The depth of the tread, in that case, would still be an issue as it would need to meet the minimum tread depth. Additionally, the tread would need to meet maximum slope allowances, and the uneven stone surface would also be a negative.

There is a landing in the above case, and that landing is the patio floor.

Just because it becomes a tread does not allow it to be free and clear of meeting code requirements, all it really does is allow the tread to be less than 36" deep minimum.

Billy Stephens
05-07-2010, 07:21 PM
Nope and nope.

(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel - looks like a 3' wide door, which means the landings would be square or deeper than they are wide.)

The uneven stone is another problem.


The depth of the tread, in that case, would still be an issue as it would need to meet the minimum tread depth. Additionally, the tread would need to meet maximum slope allowances, and the uneven stone surface would also be a negative.

There is a landing in the above case, and that landing is the patio floor.

Just because it becomes a tread does not allow it to be free and clear of meeting code requirements, all it really does is allow the tread to be less than 36" deep minimum.
.
Glad to See You Finally Come Around. :D
.

Jerry Peck
05-07-2010, 07:50 PM
You mean as long as the risers are correct the depth of the landing is not an issue?


.
Glad to See You Finally Come Around. :D
.


*I* haven't changed.

*YOU* changed the scenario.

THE ORIGINAL PHOTOS ARE STILL WRONG. :p

*YOU* changed the scenario around to *IF* ... *IF* ... all other things were correct ... and they are not ... :p :p

*I* have not changed in regard to the original discussion regarding the original post. :p

Billy Stephens
05-07-2010, 07:55 PM
*I* haven't changed.

*YOU* changed the scenario.

THE ORIGINAL PHOTOS ARE STILL WRONG. :p

*YOU* changed the scenario around to *IF* ... *IF* ... all other things were correct ... and they are not ... :p

*I* have not changed in regard to the original discussion regarding the original post. :p
'
Won't Help You there Jerry My Man. :eek:
* it was your Post that said it needs to be 36 inches not mine.

Oh and Last Word.
* unless you want to if me some more. :D

mathew stouffer
05-08-2010, 04:40 AM
Well I just put it is wrong;) For 1.7 million there should be a landing.

Markus Keller
05-08-2010, 06:39 AM
As interesting as these discussions are on the board for us HI, with situations like this I don't even bother to address the Code req. Riser height is too high, landing size is pretty much irrelevant at that point.
I would write this up as a 'hazardous' condition in my report and explain a few reasons why.
- jagged edges, uneven surface for foot transfer, apparent poor installation, unknown longevity of installation, potential trip hazard in front of glass, etc.
It's a trip hazard. How uneven will those stones be after a winter or two? Client safety is really the issue here from my perspective.
Owner probably installed the patio and or doors and forgot about the step down; thought it wouldn't be a big deal but then realized it was too high; someone thought matching the patio was a good, cheap idea since they had some left over.

Jerry Peck
05-08-2010, 08:25 PM
'
Won't Help You there Jerry My Man. :eek:
* it was your Post that said it needs to be 36 inches not mine.

Oh and Last Word.
* unless you want to if me some more. :D

Billy,

Looks like another screw up on your part - 'twas not my last post, but my first post, and it was in response to the original post, not your changed scenario, which said "needs to be 36" minimum in the direction of travel".


Nope and nope.

(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel - looks like a 3' wide door, which means the landings would be square or deeper than they are wide.)

The uneven stone is another problem.

Go back and learn to read and learn to read in the order of which the information is presented. :p Absolutely no *IF* in there about that. :D

Billy Stephens
05-09-2010, 06:21 AM
These landings were outside secondary doors and the door swing to the inside of the home. The step down is about 9 inches. Is this acceptable? Forgot to measure the dimensions of the landing.:mad:


Nope and nope.

(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel - looks like a 3' wide door, which means the landings would be square or deeper than they are wide.)

The uneven stone is another problem.


.
7 3/4 is the maximum height down. @ link under threshold.
.
International Code Requirements for Windows & Doors | Window & Door (http://www.windowanddoor.com/article/codes-standards/international-code-requirements-windows-doors)
.


Billy,

Looks like another screw up on your part - 'twas not my last post, but my first post, and it was in response to the original post, not your changed scenario, which said "needs to be 36" minimum in the direction of travel".



Go back and learn to read and learn to read in the order of which the information is presented. :p Absolutely no *IF* in there about that. :D
.
.
There You Go. ( in the order )

What Does Secondary Mean ? ( to You )

Aren't Them Be The Ones in R311.4.3 Exception 1 ? :D

Time to CleanThose Space Command Central Twin Monitors.
* or a trip to Eye Masters.;)
.

mathew stouffer
05-09-2010, 08:07 AM
I would guess they finished the house in november and didn't want to pour a pad;)

Jerry Peck
05-09-2010, 11:14 AM
What Does Secondary Mean ? ( to You )


It does not matter what secondary means WHEN THE RISERS ARE NOT THE SAME OR WITHIN THE 3/8" TOLERANCE ... when that is the case A LANDING IS REQUIRED between the two difference risers to separate them into two different flights of stairs.

Seems to me that is the part you do not get.

The other option, of course, it to make the risers equal (or within the allowed tolerance), and if that was done, then a landing would not be required there ... BUT THAT CHANGES THE SCENARIO (which is what you did) as the original photo shows the risers not being the same, which requires the landing to separate the stair into two flights of stairs, which means the risers do not have to be the same (but still would not be allowed to exceed the maximum 7-3/4" height).

Billy, first you must be able to recognize what is being shown, then recognize what is being discussed ABOUT WHAT IS BEING SHOWN, then understand what is be discussed ABOUT WHAT IS BEING SHOWN, and then be able to understand that if what is being shown is changed for the purposes of further discussion that the discussion will change based on the proposed changes.

The latter, however, in no way affects the former. The original answers STILL apply to the original discussion.

That latter answers only apply to the proposed changes discussion.

Not sure if this is too in-depth for you to follow? :p :rolleyes: :D

Billy Stephens
05-09-2010, 11:56 AM
A LANDING IS REQUIRED between the two difference risers to separate them into two different flights of stairs.
.
* no 36inch requirement ( no matter how hard you dance around it.



Seems to me that is the part you do not get.
.
I get you Stated a 36inch Landing was required were None Was.
.
Much Words with no Substance.
* Not Required ( is that too much to Admit ?) :confused:
** Is Your Day Job Clouding Your Judgment ( aka Big Head Syndrome ! ) :D
.

Jerry Peck
05-09-2010, 01:03 PM
* no 36inch requirement ( no matter how hard you dance around it.

I get you Stated a 36inch Landing was required were None Was.


Billy,

Apparently large words are too much for you. Large words such as:

(Riser too tall and landing not deep enough - needs to be 36" minimum in the direction of travel -

and

Look at those photos (and read the first post) and you will see, especially in the second photo, that the risers are not within the maximum 7-3/4" nor are the risers within 3/8" of each other.

Thus that exception is not applicable.

Is it that I used "Thus" "that" "exception" "is" "not" "applicable" and one or more of them you do not understand?

Before I can help you learn to read and understand, I need to know what it is you do not understand or know how to read. :D

Let me try to equate this thread to a more easily recognizable math problem.

Does 2+3+1=5?
The answer is "No." 2+3+1=6.

However, if you change any one of the numbers, the answer will no longer be 6, the answer will be based on whatever you changed by the amount changed.

Which is like you changing the top and bottom risers to being equal, and the landing no longer being required to be a landing, it can now be a tread.

Maybe you can follow the math better than the words?

Billy Stephens
05-09-2010, 04:34 PM
Billy,

Apparently large words are too much for you. Large words such as:


and


Is it that I used "Thus" "that" "exception" "is" "not" "applicable" and one or more of them you do not understand?

Before I can help you learn to read and understand, I need to know what it is you do not understand or know how to read. :D

Let me try to equate this thread to a more easily recognizable math problem.

Does 2+3+1=5?
The answer is "No." 2+3+1=6.

However, if you change any one of the numbers, the answer will no longer be 6, the answer will be based on whatever you changed by the amount changed.

Which is like you changing the top and bottom risers to being equal, and the landing no longer being required to be a landing, it can now be a tread.

Maybe you can follow the math better than the words?
.
Oh Now I Get It 2 + 3 + BS = BS² :D
.

Jerry Peck
05-09-2010, 07:25 PM
.
Oh Now I Get It 2 + 3 + BS = BS² :D
.

After you added all your changes and BS ... Absolutely correct! :D

Billy Stephens
05-09-2010, 08:09 PM
.
After you added all your changes and BS ... Absolutely correct! :D
.
:rolleyes: ......... :rolleyes:
.

Denny Waters
05-17-2010, 11:35 AM
The winter ice will tear those apart in no time.