What is the correct measurement between wood deck rails & the measurement for the gap between the rails & deck?

chris mcintyre
05-26-2010, 05:24 PM
What is the correct measurement between wood deck rails & the measurement for the gap between the rails & deck?

If by correct you mean maximum, 4"

Brandon Whitmore
05-26-2010, 05:38 PM
It's less than 4" allowed per current code. The code just says a 4" sphere should not be allowed to pass through.

Brandon Whitmore
05-26-2010, 05:42 PM
http://www.stairways.org/pdf/2006%20Stair%20IRC%20SCREEN.pdf

Jerry Peck
05-26-2010, 07:12 PM
simply highlighting the critical part ;)


If by correct you mean maximum, 4"


It's less than 4" allowed per current code. The code just says a 4" sphere should not be allowed to pass through.

chris mcintyre
05-26-2010, 08:00 PM
It's less than 4" allowed per current code.

Does it count if I was thinking "less than"????

Jon Errickson
05-27-2010, 05:42 AM
Thanks for the great PDF document Brandon!

Brandon Whitmore
05-27-2010, 09:14 AM
Does it count if I was thinking "less than"????

Wasn't that you that said you must limit giving out misinformation to one post per topic:D You met your quota is all.


Thanks for the great PDF document Brandon!

No problem. I wish they had visual interpretations written up that covered other areas as well.

Brent Crouse
05-28-2010, 05:21 AM
From Brandon's pdf (photo 17), does the following apply to deck stairways as well?

"Open risers are permitted, provided that the opening between treads does not
permit the passage of a 4-inch diameter (102 mm) sphere."

Seems like this would be a problem for just about every deck with a stairway having 30" rise or more.

Brandon Whitmore
05-28-2010, 11:40 AM
From Brandon's pdf (photo 17), does the following apply to deck stairways as well?

Yes..