View Full Version : Condensate trap too big?
Jon mackay
06-14-2010, 01:48 PM
This condensate trap for an A/C connection seemed a bit too large but I wasn't sure if it was actually wrong.
Is there a limit to the size?
Rick Hurst
06-14-2010, 02:23 PM
Jon,
Ever try and push water uphill?
Yes, its wrong.
rick
Billy Stephens
06-14-2010, 02:23 PM
.
actually wrong.
.
.
On So Many Levels.
.
Mike Gault
06-14-2010, 02:34 PM
And leaking, it appears...
Michael Thomas
06-14-2010, 03:00 PM
See attached:
David Bell
06-14-2010, 05:19 PM
Very wrong, but probably works as the coil is probably about 4.5' off the ground.
Corn Walker
06-17-2010, 03:23 PM
Ever try and push water uphill?
The Romans did it centuries ago. But unless that's intended to be an aqueduct yes, it's wrong.
Markus Keller
06-17-2010, 03:52 PM
Ummm, size would appear to be the least of the problems. That's really a beautiful set-up. So do those pipes go down into a crawl? Looks like a great rodent highway.
Trent Tarter
06-17-2010, 09:53 PM
It's all wrong, what it needs is a condensation pump with a drain line that is routed overhead and into the PVC drain pipe.
Rich Goeken
06-18-2010, 03:35 AM
It's all wrong, what it needs is a condensation pump with a drain line that is routed overhead and into the PVC drain pipe.
I tend to disagree with this "quick Fix". My experience with condensation pumps is that it's another point of failure. They tend to quit a lot, and its usually an item that may be looked at one a year if you are lucky. This should be a last resort if a good condensation gravity system can't be installed.
Jane Slaughter
06-18-2010, 06:08 AM
Besides the length of the drain 'trap"; Isn't a condensate trap supposed to have an air gap(?) and not be directly connected to the sanitary sewer?
jason schatz
06-18-2010, 08:42 AM
Besides the length of the drain 'trap"; Isn't a condensate trap supposed to have an air gap(?) and not be directly connected to the sanitary sewer?
was thinking the same thing --- until I saw what looks like a cleanout is actually an AAV...
Corn Walker
06-18-2010, 09:39 AM
was thinking the same thing --- until I saw what looks like a cleanout is actually an AAV...
an AAV is not an air gap, it does nothing for backflow prevention
jason schatz
06-18-2010, 09:45 AM
you're right, my fault...
Vern Heiler
06-18-2010, 10:09 AM
Besides the length of the drain 'trap"; Isn't a condensate trap supposed to have an air gap(?) and not be directly connected to the sanitary sewer?
Does condensate water qualify as cross connection to portable water?
Corn Walker
06-18-2010, 10:16 AM
Does condensate water qualify as cross connection to portable water?
Potable water contamination is one but not the only reason to have a backflow/backpressure preventer.
jason schatz
06-18-2010, 10:18 AM
seeing as there is no potable water connection at the heater, I'd say that'd be a no....
But sewage backflow...even if it were just gases...wouldn't be a nice scene in the air flow of the unit.
David Bell
06-18-2010, 12:37 PM
The requirement for condensate is much the same as effluent, trapped at the closest place and subject to venting requirements.
Wayne Carlisle
06-18-2010, 01:27 PM
Where is the specification that the horizontal piece of a trap cannot be 6"...12" or even 96" on a condensate line.
I looked at the links provided and all that was specified was height requirements. Nothing about from one vertical to the other.
Please educate me.
David Bell
06-19-2010, 05:50 PM
The condensate piping by itself is only subject to condensate guidlines. But once you connect that to a homes DWV system, it must adhere to all codes and regulations that all piping in that system conforms to.
Wayne Carlisle
06-21-2010, 09:15 AM
Okay....so you are saying what?
David Bell
06-21-2010, 03:40 PM
Okay....so you are saying what?
The trap lengths and heights are subject to plumbing codes
Michael Thomas
11-20-2011, 03:45 PM
WRT the necessity of traps on the suction side of air handlers, this may be of interest:
Condensation in ceiling - Contractor Talk HVAC forum (http://www.contractortalk.com/f6/condensation-ceiling-101150/)
Powered by vBulletin® Version 4.2.0 Copyright © 2025 vBulletin Solutions, Inc. All rights reserved.