View Full Version : Electrical panel
Wade Johnson
06-23-2010, 01:54 AM
Good morning. What is happening when some of the breakers in a panel are warm or even hot to the touch?
Jim Port
06-23-2010, 05:18 AM
Heat is generated by the current flowing through the breaker. This heat is what causes a breaker to trip on overload.
Abnormal levels of heat could point to a problem.
Michael Thomas
06-23-2010, 07:13 AM
Were they AFCI breakers?
Michael Thomas
06-23-2010, 07:14 AM
Heat is generated by the current flowing through the breaker. This heat is what causes a breaker to trip on overload...
Well, at least in many modern designs, not exactly, see for example:
HowStuffWorks "Basic Circuit Breaker Design" (http://electronics.howstuffworks.com/circuit-breaker2.htm)
Bill Kriegh
06-23-2010, 08:32 PM
Most all breakers of modern manufacture (that you're likely to find in a residence) have both a magnetic and thermal component to the trip mechanism.
An illustration that does not reflect actual trip curves but illustrates the point is a 15 AMP breaker may carry 16 Amps for many hours before tripping, but will trip much sooner with a 30 AMP load.
The magnetic component makes for instant tripping when a fault occurs.
Older breakers may lack the magnetic component
Gunnar Alquist
06-23-2010, 08:49 PM
Good morning. What is happening when some of the breakers in a panel are warm or even hot to the touch?
If there were lots of high intensity lights on for a long time, it might explain the problem. A Zinsco/Sylvania panel might be arcing at the buss bar connection. I would defer and have an electrical contractor look at it.
Jon mackay
06-30-2010, 05:22 AM
I had an electric water heater turn on while I was inspecting a panel and the 30 Amp breaker heated up to about 100 degrees.