View Full Version : Pressure treated for wall studs
Richard Flores
07-15-2010, 12:18 PM
Can a load bearing wall have pressure treated studs or are the only allowed to be used for bottom plates.
Wayne Carlisle
07-15-2010, 12:28 PM
I don't see any problem with it. PT wood is just regular wood that has been treated.
That is an interesting question though!
Richard Flores
07-15-2010, 12:42 PM
Thanks for the quick reply. A typical homeowner that claims he was a contractor said that you can't use it. I had never heard of it, so I guess I am going to have to look at my Code book..
Wayne Carlisle
07-15-2010, 12:48 PM
As long as the PT lumber is grade stamped....I don't see a problem.
From the 2006 IRC
SECTION R602
WOOD WALL FRAMING
R602.1 Identification. Load-bearing dimension lumber for
studs, plates and headers shall be identified by a grade mark of
a lumber grading or inspection agency that has been approved
by an accreditation body that complies withDOCPS 20. In lieu
of a grade mark, a certification of inspection issued by a lumber
grading or inspection agency meeting the requirements of this
section shall be accepted.
R602.1.1 End-jointed lumber. Approved end-jointed lumber
identified by a grade mark conforming to Section
R602.1 may be used interchangeably with solid-sawn members
of the same species and grade.
R602.1.2 Structural glued laminated timbers. Glued
laminated timbers shall be manufactured and identified as
required in AITC A190.1 and ASTM D 3737.
R602.2 Grade. Studs shall be a minimum No. 3, standard or
stud grade lumber.
Exception: Bearing studs not supporting floors and
nonbearing studs may be utility grade lumber, provided the
studs are spaced in accordance with Table R602.3(5).
Richard Flores
07-15-2010, 12:49 PM
Thanks..That is exactly what I was looking for... :)
chris mcintyre
07-15-2010, 06:04 PM
It may not be a code issue but IMO it is not a good idea for a couple of reasons.
1) Treated lumber shrinks as it dries and not at the same rate. You can cut the ends of the decking boards in a straight line and 6 months later they will vary in length a 1/2" or more.
2) If you use PT studs you would have make sure everyone was using the right fasteners for sheathing, wall ties, siding, drywall, trim, cabinets, etc...
Elliot Franson
07-16-2010, 10:08 AM
With the known shrinkage and warpage issues in CCA and other pressure-treated dimensional lumber, it would be unwise, in my opinion to use this for wall studs. Just my opinion.
Powered by vBulletin® Version 4.2.0 Copyright © 2025 vBulletin Solutions, Inc. All rights reserved.